Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
mr leak (CA)
Anyone have concerns about using a "sharkbite" connector fitting behind drywall ?
|
Post Reply
|
Author:
hj (AZ)
Not as long as that is the only way to fix something.
|
Post Reply
|
Author:
bernabeu (SC)
YES
IMO: DON'T
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
solventwelder (GA)
@bernabeu Why not?
|
Post Reply
|
Author:
bernabeu (SC)
because a hidden, inaccessible, "O" ring seal held by a 'tensioned gripper' on a pressurized line is not good practice
nor even code compliant (most codes)
i feel the same way about PEX fittings, albeit code compliant they are not 'best practice'
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
However, I just read that "best practice" in Chicago is STILL lead/oakum joints and maximum 5' soil pipe lenghts.
|
Post Reply
|
Author:
steve (CA)
specifically allows "push fit fittings" under section 605.3.3.3 and doesn't specify that they have to remain accessible. (I wouldn't use them hidden in a wall)
|
Post Reply
|
Author:
hj (AZ)
Sometimes what the code requires or allows is NOT the best practice, however.
|
Post Reply
|
Author:
bernabeu (SC)
... nor even good practice
OMG
hj and I agree on something
the pigs have actually flown
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: