Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Weil Mcclain boiler with indirect water heater issue
Author: dr057 (NY)

Hello,

I have a weil mcclain gold oil fired boiler with a PHCC 9048-609 indirect water heater. It's about 10 yrs old. The problem I'm seeing is after the hot water gets used up in the tank it seems to take a very long time (maybe an hour or so) for the hot water to regenerate.

It has 3 zones and one is the hw zone and all 3 zone valves were replaced recently so I know the valve is working fine.

What may be causing it to take so long for hot water to generate, could there be an issue with the PHCC controls?

Thanks, Dean

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: packy (MA)

how do you know the zone valve for the domestic hot water is working fine?
have you felt the pipe supplying boiler water to the indirect when the domestic hot water runs low?
is there a 'zone control' relay controling the 3 zones?
what is the high limit on the boiler set at?

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: dr057 (NY)

how do you know the zone valve for the domestic hot water is working fine?

I felt the pipe going to boilermate and it's hot.

have you felt the pipe supplying boiler water to the indirect when the domestic hot water runs low?

I think when water runs low the piep still feels hot, but I'll chk that next time I can.

is there a 'zone control' relay controling the 3 zones?

I don't know, how do I find out?

what is the high limit on the boiler set at?

It's set to approx. 180.

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: m & m (MD)

Are there any 'hidden', or otherwise, leaks in the HW distribution?

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: dr057 (NY)

No, no leaks. And just recently had 3 zone valves replaced, 3 safety valves, expansion tank and inlet flow valve. The hot water is fine, it just seems to take long for it to detect that all hot water is gone and needs to be regenerated. That's why I was thinking maybe the boilermate thermostat-aquastat control is going bad?

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: Paul48 (CT)

As for a zone control....You're looking for a box that your thermostat wires run to. If you don't have one, there is now way to give priority to DHW, and the boiler may be trying to satisfy a heat zone at the same time it tries to heat the hot water.

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: Paul48 (CT)

Ahhh..........Read the manual for the indirect, I'd bet the new zone valve is too small. What's the make and model of the zone valve for the indirect?



Edited 1 times.

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: m & m (MD)

Wouldn't the plumber simply match the new zone valve to the one he was replacing? ( He may have only replaced the power heads.)

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: Paul48 (CT)

Maybe we should get the whole story...from the beginning. Did the indirect ever work correctly? Why were all 3 zone valves replaced. The PHCC is not the model of the boilermate, refer to the manual. Help us and we'll help you figure it out.

Post Reply

 Re: Weil Mcclain boiler with indirect water heater issue
Author: dr057 (NY)

Hi Paul, the zone valve that was replaced is same size as new one, I don't think that's it but I think I may have found the answer. Looking at the 2 wire that runs from the boilermate where the hot water zone was replaced the wire was scraped off on one side and when I move it around I can hear the valve clicking on and off so may be the problem. I'll put a new wire in and tighten all conections and see what happens.

All 3 zone vavles were replaced due to valves were sticking and I was burning out zone motors.

Thanks for your help!



Edited 1 times.

Post Reply

 Thanks everyone for your help, much appreciated! clap
Author: dr057 (NY)

Yeah that seemed to have been the issue, a chaffed wire leading from boilermate aquastat to control valve. After fixing the wire the hot water is back to normal..

Thanks everyone for your help, much appreciated!



Edited 1 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.