Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Watts galv. steel water heater enclosure.
Author: 949holt (CA)

Hi, I've got a dilemma with venting an exterior water heater enclosure.

In it there's a direct vent 40gal gas water heater.

The enclosure is 24"x 24"x 72" and mounted on a 12" riser of concrete.

The top of the box has about 22" clearance under the eave.

The eaves are really deep about 30" from fascia to wall.

Currently it is vented with 3" accordion flex to single wall and strapped

to the fascia with an 18" riser above the roofline to a standard vent cap.

Needless to say it looks god awful and I don't believe it is venting correctly.

I don't want to cut through the eave to run it straight up.

Is it legal to just 90 it off the top and vent horizontally?

Or maybe fabricate a heat shield under the eave and just stub it out short?

The location is in a breezeway between 2 houses, but when there is a no wind situation

I'm guessing there could be some C02 issues? It would however be venting approximately 8' off the ground.

Any suggestions would be greatly appreciated, Thanks

Post Reply

 Re: Watts galv. steel water heater enclosure.
Author: packy (MA)

you need to use B-vent for a chimney.
regular smoke pipe must have 6 inches clearance fron wood.
B-vent can be within 6 inches of wood.
you can not put a 90 directly on top of the draft hood. must be at least 12 inches of straight pipe before turning 90 deg.
maybe have a talk with you gas inspector about how to run the chimney legally.

Post Reply

 Re: Watts galv. steel water heater enclosure.
Author: hj (AZ)

If you vent it horizontally, the wind will blow into it and cause combustion and pilot issues.

Post Reply

 Re: Watts galv. steel water heater enclosure.
Author: steve (CA)

You stated the water heater is a "direct vent". Is this correct?

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.