Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
need for knowledge (CA)
The home is set back off the property 100 ft and has a drop of about 15ft. at that point. The sewer line st the street is 8ft below grade. Is there anyway this house will not need to use a pump for sewage?
|
Post Reply
|
Author:
North Carolina Plumber (NC)
If you're going to be 7' under the sewer, then yes a pump will be required.
|
Post Reply
|
Author:
packy (MA)
i believe he is saying there is a total 23 feet of drop ... 23 x 4 = 89. so at 1/4 inch per foot you will not make it. but at 1/8 inch per foot you will be fine.
|
Post Reply
|
Author:
toocute350 (LA)
As long as your house is above the street you should be fine.Remember water flows with gravity.If your sewer line has to travel up, it won`t drain.
|
Post Reply
|
Author:
hj (AZ)
No way to tell what he means by "15' drop at that point", but if the house is below the sewer line, under the current laws of physics, he will need a pump.
|
Post Reply
|
Author:
hj (AZ)
You are working backwards. The distance is 100' which requires TWENTY FIVE INCHES, (NOT 25 FEET), of fall at 1/4"/foot
|
Post Reply
|
Author:
packy (MA)
the laws of physics must be different between AZ and MA. but in either case you are correct. i stand with hat in hand even though i was only off by a factor of 12...
|
Post Reply
|
Author:
hj (AZ)
the laws of physics must be different between AZ and MA.
Must be because of the Kennedys.
|
Post Reply
|
Author:
packy (MA)
actually it is the fault of the 'big dig'. there are so many unfixable leaks that it is affectionately known as the worlds largest car wash.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|