Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 oil tank replacement
Author: northern (NY)

so along with replacing my 70 year old heating system is the replacement of the 275 gallon tank above ground in the garage ,I pumped out the remaing 6 inches of fuel oil ...dragged it outside and took a sawzall to it and cut it in half .Scrap guys came and its history [i wonder if i could of left it ..we seem to throw so much out in this country ]Anyway the existing copper tubing goes from garage in concrete floor aprox 15 feet to boiler room .ive been advised to not reuse it.So i have to buy a tank and was told i can run a new copper tube from tank to boiler room but overhead and a two pipe or tube system .Can anyone explain this set up?The old tank had one outlet on it do i need to buy a tank set up for this two pipe deal ?Any other ideas?

Post Reply

 Re: oil tank replacement
Author: m & m (MD)

The two pipe oil system utilizes a supply and return line from/to the tank. Its advantage is that you rarely 'lose prime' but its BIG disadvantage is that for every gallon of oil that you supply to the burner, nine gallons are being returned to the tank. Result: more turnover = more oxidation = quicker sludge accumulation.

If your oil tank is higher than the burner, I suggest finding a way to make a single pipe system work even if it means relocating the tank.

Post Reply

 Re: oil tank replacement
Author: northern (NY)

Interestimg ...yeah i poured a 3inch pad for the new boiler so it still will be lower then the tank .I guess i will be busting up some concrete to run a new one line .Is there a coated copper available for undergroud?

Post Reply

 Re: oil tank replacement
Author: m & m (MD)

Is it possible to run the line around the perimeter of the garage floor to the burner?

Post Reply

 Re: oil tank replacement
Author: northern (NY)

no it would be like a 80 foot run .

Post Reply

 Re: oil tank replacement
Author: bernabeu (SC)

... or similar ...



==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: oil tank replacement
Author: packy (MA)

you can run the oil line overhead for that short a distance (15 feet) with no problem. just have to make sure there are no leaks. the oil burner pump will pull air into the copper and the flow will stop.
roth tanks are piped like this all the time. in this picture the tubing runs down to within a inch of the bottom. your tank will feed from the bottom, run up to the ceiling and over and down to the burner. use the copper tubing with the orange jacket to conform to code.

Post Reply

 Re: oil tank replacement
Author: Paul48 (CT)

packy...Does it have to be a 2 stage pump on the burner? I don't know much about oil burners. I leave them to the pros. I can only parrot what I have read. Aren't some burners problematic when run over head? I have read that the cure for this problem, is something called a tiger loop?

Post Reply

 Re: oil tank replacement
Author: packy (MA)

back a few years ago the insurance companies were refusing to insure a home's oit tank etc if the copper was not sheilded. so, all the oil ilnes that were plain old copper buried under cement had to be replaced. lots of work for me and the oil men around here.
some lines could be replaced and encased in liquid-tite others had to be run over head. dozens that i did overhead were fine just as they were.

Post Reply

 Re: oil tank replacement
Author: northern (NY)

what was that bern showed ?A threshold to use in front of doorways to hide and protect tubing?....PACKY..are you saying i dont need a two pipe system ?That because its a short distance the oilburner will pull the oil?

Post Reply

 Re: oil tank replacement
Author: northern (NY)

Also packy do you have an opinion on reusing the existing tubing that is in the concrete 70 years old ?Just curious how a pro would approach it

Post Reply

 Re: oil tank replacement
Author: m & m (MD)

One stage pump will do fine on most residential. With one pipe system that is higher (and even on plane) than the pump, if any air at all is introduced, the pump will lose prime. The Tiger Loop is made just for that condition and prevents airlock.

Post Reply

 Re: oil tank replacement
Author: packy (MA)

i would not use the tubing under the floor. just use some of the orange jacketed copper tubing and run it overhead.
the new oil tank will have a 1/2 inch tapping on the bottom and none on the lower side. use a special (not expensive) oil tank valve. dope up the threads, screw it into the bottom, screw on a cartridge type oil filter, screw a 3/8 flare x male adapter into the filter then run the tubing to the burner. at the burner you want a 3/8 inch LONG angle firomatic valve.

reuse the 1 1/4 steel fill and vent if you want. nothing goes wrong with it. do get a new combination tank gauge and whistle.
lastly, do not pipe the 1 1/4 fill so when filling the oil dump ontop of the cork float..

Post Reply

 Re: oil tank replacement
Author: bernabeu (SC)

Quote

what was that bern showed ?



Floor mounted 'raceway' generally used to protect electric cables, but also available to act as a 'trench'.

The good (expensive) stuff is sectional and interlocks to make 'runs' - the 'tab ends' not needed for interlocking would be cut off for a good finish/look if needed.

If sized well for 3/8 tube it would not present more of a tripping hazard than the tube itself, less in fact.

another example:





==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: oil tank replacement
Author: m & m (MD)

Packy, You're still using 1-1/4" fill and vent? In MA????

Post Reply

 Re: oil tank replacement
Author: Paul48 (CT)

What do you use down there? I see 1 1/4 or 1 1/2 here.

Post Reply

 Re: oil tank replacement
Author: m & m (MD)

2" fill and vent required for the last twenty years or so to reduce excessive pressures on tank from high flow delivery rates.

Post Reply

 Re: oil tank replacement
Author: Paul48 (CT)

As far as I know, the only change here, was to require the same size vent as fill.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.