Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
sum (FL)
I had a central AC broke down and I called in an AC service company to fix.
Turned out all the refrigerant leaked.
It leaked because of a hole in the copper line.
The hole was formed due to an electrical arc caused by an electrical conductor inside the compressor box broke off the wire nut and touched the copper line.
and the breaking off from the wire nut was caused by the humidity...the metal "spring" inside the wire nut corroded.
The AC tech brazed the hole and sealed the hole...is this the right way to fix it instead of using some copper sleeve?
|
Post Reply
|
Author:
m & m (MD)
I'll do the same thing sometimes with copper pipe that has frozen and ruptured. Works fine.
|
Post Reply
|
Author:
packy (MA)
real brazing is stronger than the copper tubing.
|
Post Reply
|
Author:
sum (FL)
But essentially it is like plugging the hole with solder right?
I thought a better fix would be to cut out a short piece then put in a longer repair coupling and braze the two joints.
No big deal just wanted to make sure this is ok.
|
Post Reply
|
Author:
packy (MA)
sum, you have to understand how strong brazing is..
plumbers soft solder fittings to pipe at a temperature of slightly over 400 F deg.
brazing requires a temperature of 1350 F or more.
as i said, done properly the brazing is stronger than the tubing..
|
Post Reply
|
Author:
hj (AZ)
That would be a much more difficult process than you think it would be, and immensely more expensive.
|
Post Reply
|
Author:
bernabeu (SC)
right on, hj - IMMENSLY more $$$$$
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
sum (FL)
why would it be much more difficult and expensive? I am not saying what's done was inferior, I am OK after Packy's explanation.
But why would using a sleeve to repair be a much more difficult task? Isn't that just soldering on steroid? I know I can solder a repair coupling to a copper line in about 10 minutes and I am someone who moves at turtle speed, so an experienced AC tech should be a piece of pie NO?
|
Post Reply
|
Author:
hj (AZ)
NO! to cut the line and install a coupling would require evacuating the system into a storage contaniner, brazing the coupling probably while pumping the system down, then replacing the gas. And, that assumes he has room to insert the coupling and access all the way around the tubing.
Edited 1 times.
|
Post Reply
|
Author:
sum (FL)
OK, but in my case, the refrigerant has leaked out totally, it was at 0 psi, so there was nothing to put away and store...but I got the point now, thanks.
|
Post Reply
|
Author:
KCRoto (MO)
Soft tubing isn't always round anymore, so it can take time to reshape it back to where it needs to be if you were to try to solder it as well.
|
Post Reply
|
Author:
hj (AZ)
He would still have to evacuate since not ALL of the refrigerant leaked out and the heat of making the coupling joints would have "vaporized" the gas and caused an internal pressure which would have caused the joint to fail as it was "blowing out".
|
Post Reply
|
Author:
bernabeu (SC)
evacuate and (for best practice) purge while brazing with dry nitrogen or argon
or
what he did (99.99% effective)
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
hj (AZ)
What, you mean you do not like the Phosgene gas generated by heating the refrigerant red hot?
|
Post Reply
|
Author:
bernabeu (SC)
loooove the Phosgene, haaaate the compressor damage from the flakes of Cuprous Oxide
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
Hodrick (AR)
Hi, it would be interesting to know if something helped you from the tips given in the comments above. I ran into a similar problem with air conditioners, and I can't even imagine what the problem might be and what I should do. I want to solve it all on my own and for free, but maybe I need to use the services of professionals. I'm thinking of turning to [airconrepairservice.com] since a friend said they repaired her air conditioners, and then everything was fine with them. Has anyone heard about this service?
Edited 2 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|