Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Pressure relief valve
Author: lewisj95 (UT)

I have rheem gas water heater and I am getting water out the PRV. I have replaced the valve and still getting the leak. On the thermastat dial is an arrow then a A B C. I have mine set on the arrow and im getting 140 degrees from faucet. The manual says it should be 120 on the arrow setting. Could I have bad temp gauge or expansion tank or....?
The water heater is 2 yrs old.

Post Reply

 Re: Pressure relief valve
Author: KCRoto (MO)

If you are getting 140 degree water from the faucet, then you need to look at the pressure first. Yes, it could be a combination of issues causing a temperature spike in the tank, but it is unlikely since the water is 140 at the faucet. Use a pressure gauge and attach it to a hose faucet after your pressure reducing valve and check the pressure. Let a couple gallons of water out first to be sure it hasn't climbed while it is sitting there. If the pressure is high, your prv is bad. If the pressure is at the prv's set point, then the expansion tank is bad. If the Prv is bad, it can still be an expansion tank as well.

Post Reply

 Re: Pressure relief valve
Author: lewisj95 (UT)

i have tested pressure at hose bib and HWH spicket and both are 70

Post Reply

 Re: Pressure relief valve
Author: Doug E. (CA)

what pressure do you read on the expansion tank?

Post Reply

 Re: Pressure relief valve
Author: KCRoto (MO)

With the water to the house off and the pressure drained at a faucet, check the pressure in the expansion tank with a air pressure gauge. If you press on the schrader valve and water squirts out, the tank is bad; if not, the pressure in the tank should be at ~75 psi to work properly. A bicycle air pump can be used to fill up the tank.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.