Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
mrhaneysr (FL)
I have an old home the house has settled 8 inches. (Florida Cracker home built on cement pillars) The 4 inch septic line has a negative pitch (3 inches )coming out of the home (first 4 feet) then ok. We have only one toilet on this 4 inch line line (Grey water diverted). The line runs 66 feet.
Will it flow with out assistance? What the best fix with out tearing it out?
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
assuming (I know I know) the line was originally properly pitched at 1/4" per foot it had a 'fall' of 6.6"
if it had been 'minimally' pitched at 1/8" per foot you had 3.3"
you are now negatively pitched
you WILL need to correct the situation
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
mrhaneysr (FL)
Checking the rest of the line it looks like 1/8 inch. Would a added 2" sewage grinder system ( like Liberty Pumps P382LE51 1/2-Horse Power 24 by 24-Inch Pro380 Series Simplex Sewage System) fix it?
|
Post Reply
|
Author:
North Carolina Plumber (NC)
A pump would "fix it", but you'll need a catch basin, and a vent for it. The pump will eventually give trouble and have to be replaced.
There's no way to raise the first 4' of pipe ?
|
Post Reply
|
Author:
m & m (MD)
Have you had problems already with stoppages? If not, why not wait and see if you will? The settling didn't happen overnight so it's been operating under those conditions for some time. The sewage pump makes sense in your situation but it should be noted that that model is NOT a grinder pump, simply a sewage pump.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: