Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
bernabeu (SC)
[www.ashireporter.org]
Trap problems
When a trap seal is too shallow, it can be sucked or blown dry at each cooling cycle startup. Running traps are prone to fail in this way. Some manufacturers specifically recommend against the use of running traps.
If the seal is too deep, it actually can cause condensate to be held in the pan. A trap with an excessively deep seal also is prone to clogging. Because fan speed, duct size, coil condition or other issues that affect the static pressure around a cooling coil can be as varied as each HVAC system installation, trap design should be as varied as well. Based on my experience as an installer and service tech, I believe little consideration actually is given to static pressure issues, and though traps might appear to be somewhat different from unit to unit, this almost certainly is from happenstance and almost never by engineering or design.
translation: Follow the manufacturer's instructions. D'OH
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
quote; If the seal is too deep, it actually can cause condensate to be held in the pan.
NOW, how could that happen. The difference in elevations between the inlet and outlet are what cause water to flow through a trap. The DEPTH of the seal is immaterial, because when water flows into it on one side, it raises the level on the other side, REGARDLESS of how deep the seal is and thus the same amount of water flows out of the trap. It is just NOT the same water that flowed in however, which it seldom is in any trap anyway unless it is a large flow.
|
Post Reply
|
Author:
bernabeu (SC)
the seal depth should be 2" + whatever maximum static pressure the unit can develop
since the 'typical' unit runs at .25" with a clean filter and up to 1" with a dirty filter
a typical trap 'should' have a 3" seal
no one can really explain how or why, but, from industry experience, a trap with a too deep seal WILL create problems
IMO: this is due to NOT increasing pipe size as soon as you 'drop' into the trap
ie. 3/4" tapping in unit should be piped horizontal 3/4 into a 1" trap (running full 1" thereafter)
wires on top are for alarm/cutout - shown being brush cleaned using vent port which is normally open to atmosphere on DISCHARGE side of trap
height difference between inlet and outlet is to allow for friction loss and to build a 'head pressure' for drainage in spite of static developed pressure (suction)
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 2 times.
|
Post Reply
|
Author:
hj (AZ)
whatever as long as you use your own laws of physics and hydraulics.
|
Post Reply
|
Author:
bernabeu (SC)
and you, of course, are more knowledgeable than EVERY HVAC manufacturer
check with
Trane
Carrier
York
Lennox
even Goodman
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
KCRoto (MO)
Is this really an issue? Most hvac installers use the preformed pvc traps that have about a 1.5" water seal on them anyhow, and many that I have seen a open Tee somewhere above them for air admittance or cleaning.
|
Post Reply
|
Author:
hj (AZ)
Not disagreeing with the recommendations, just YOUR interpretation of why it is done that way.
|
Post Reply
|
Author:
bernabeu (SC)
sorry, perhaps I was a wee bit 'touchy'
however
they are NOT recommendations
they are manufacturer's REQUIREMENTS
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|