Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
nelson07 (NY)
Okay, I have an old farmhouse and am trying to add a bathroom upstairs. The stringers are a true 2x8. I have to run the toilet line between two 8" stringers for about 14 feet. Therefore I plan on using 3" pipe so I get enough drop in the line. Between the toilet and the drain going to the basement. I was planning on looping in 2 in drains from the shower and a sink about 6 feet from the toilet.
Where the drain drops to the basement I was planning on T'ing the line and running a 3" vent straight up through the roof.
Suggestions or comments...will it work?
Also thought maybe I should do the shower seperately and take the 2" drain right into 3" where it drops?
I
|
Post Reply
|
Author:
steve (CA)
Will it work and what is legal are two separate things. It would not be legal to have the vent that far away from the fixtures. You can accomplish this closer venting with a wet vent or separate fixture vents. We would need more info in the way of pictures/drawings to help with this.
|
Post Reply
|
Author:
packy (MA)
it will work but it won't be even close to code..
run your 3 inch to the toilet. put a 3 x 2 "Y" for the tub. in that 2 inch going to the tub put a 2 inch "Y" for the sink. put a san tee into the vertical 2 inch pipe for the sink drain and run a pipe from the top of that san tee up thru the roof.
classic wet vent..
|
Post Reply
|
Author:
hj (AZ)
It will "work" but it will NOT be venting any of your fixtures.
|
Post Reply
|
Author:
nelson07 (NY)
Soo glad I posted here!
Okay, here is my original thought here. Where I have "drops to basement" is where I was going to T the 3" line and take it through the roof.
[www.dropbox.com]
What I am hearing is to do it this way....please advise.
[www.dropbox.com]
Thanks,
|
Post Reply
|
Author:
packy (MA)
you are getting closer. the vent for the vanity can not come from below the floor.
you must keep that drain 2 inch in size and run it up the wall behind the vanity. put a 2 x 2 x 1 1/2 sanitary tee inside the wall at 19 inches off the floor and run a 2 inch pipe off the top and up thru the roof.
as i said before, classic wet vent..
|
Post Reply
|
Author:
hj (AZ)
The second one is better, if you can get the pipes crossing inside your floor and the lav connected to the vent ABOVE the floor.
|
Post Reply
|
Author:
steve (CA)
In drawing #2, you have the wet vent crossing over the top of the 3". I don't think you're going to have the room in an 8" joist bay to fit it in(or it's going to be very close). Drawing #1, with both the shower and vanity being vented would work.
|
Post Reply
|
Author:
nelson07 (NY)
Okay, agreed. I will never get the 2" over the 3" pipe. How about this...I have both the sink and the shower dumping into the 3" line but I will have the wet vent on the sink 18" up the wall and out the roof.
[www.dropbox.com]
on another note, this house had no vent at all on the little bit of plumbing that was there downstairs. Should I take the 3" pipe out the roof as well where it t's into the floor or is this just a lot of work for nothing.
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
if you have no full size vent going thru the roof, put a 3 inch sanitary tee where the drain comes up from below and call that the main vent stack.
also do as you have drawn and vent the lav with 2 inch so it wet vents the toilet. the tub will need to be vented as well..
bring your smaller vents back and tie into the 3 inch vent stack. this way you will have only one roof penetration..
|
Post Reply
|
Author:
hj (AZ)
Shower is NOT vented, and the way you have it drawn neither is the lavatory.
|
Post Reply
|
Author:
nelson07 (NY)
Okay, trying to figure this out. Can I vent the toilet by tieing it in to the wet vent for the sink? For the shower can I put a second line out to the 3" pipe going out the roof? Per the picture.
[www.dropbox.com]
OR THIS? Better Idea...
[www.dropbox.com]
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
NEither one of those would be acceptable the way you have them drawn. Now do you see why DIYers have problems trying to do their own remodeling. IT is more than just buying some fittings and pipe, then gluing them together.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|