Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
pbr2424 (NH)
I was wondering about a what if situation. If you had heating main in a commercial biulding that were 200 feet long with 2 inch black iron pipe and someone added twelve 90's
that were black iron in order to go up and over objects in three places on just the supply plus the return woudn't the added resistance of the fitting throw off the engineers calculations for the pipe sizing plus the idea of air being caught in the system. I would think that going up and over objects three times with 90's would change what an engineer would of had in mind. Appreciate any help.
Thank you
|
Post Reply
|
Author:
hj (AZ)
IN most heating systems the velocity is maintained at a low gpm so that would not compromise the calculations, UNLESS they were right on the cusp of the flow rate. Air, however is a different story, because that same slow flow may not be enough to push air out of any elevated area.In fact, the slow flow would have a tendency to "drop" any entrained air at a high spot in the piping.
|
Post Reply
|
Author:
pbr2424 (NH)
How would you eliminate the air. With an auto vent on the top 90's or avoid the situation with 90's use 45's. and still use venting. Have the engineer sign off would be best on whatever is used.
Thank you
|
Post Reply
|
Author:
hj (AZ)
A high spot WILL collect air, regardless of whether it was made with 90s or 45s. A tee in place of one of the elbows at each high spot would be a place for an air vent.
|
Post Reply
|
Author:
pbr2424 (NH)
Appreciate your response. Will have to look into it some more.
Thank you
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: