Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
440molson (OH)
Does anyone know the ohio code, that would verify if a grease interceptor can be used as a floor drain, or if a floor drain can tie into it? If so, can someone post it please.
|
Post Reply
|
Author:
hj (AZ)
There is no way it could be used AS a floor drain, but if the floor drain is in an area where grease or oil could flow into it, such as a garage, it would have to be connected to a grease interceptor or "triple basin" collector.
|
Post Reply
|
Author:
440molson (OH)
So, a seperate floor drain can tie into the grease intercepter? I can't find a code to verify this.
|
Post Reply
|
Author:
packy (MA)
as my friend from AZ said, if a commercial kitchen has a floor drain in close proximity to any of the sinks used for washing dishes, that floor drain must empty into a grease interceptor..
|
Post Reply
|
Author:
hj (AZ)
IT would be under the garage drainage area.
|
Post Reply
|
Author:
440molson (OH)
Sorry, I didn't clarify earlier. This is for a restuarant kitchen. They don't have a drain in the area. So, they will need to install a drain, and are able to tie into the interceptor. That is good, thank you. I cannot find an Ohio, nor International code that says that I can't use the interceltor as a drain, nor connecting a fd to the interceptor.
Thanks in advance, Marc
|
Post Reply
|
Author:
hj (AZ)
To use the interceptor "as a drain", it would have to have an 'open' top, which is impossible. since the interceptor MUST be connected to a drain line, you can either run the floor drain through the device, or connect the floor drain before the interceptor.
|
Post Reply
|
Author:
440molson (OH)
Thank you both, for your help.
|
Post Reply
|
Author:
440molson (OH)
There is a 3-compartment sink, and they are wanting to use that drain, that goes to the interceptor, as a floor drain, also. Sorry about the lack of information. They are trying to avoid cutting the floor to install a floor drain.
|
Post Reply
|
Author:
hj (AZ)
??? Won't they have to cut the floor for the floor drain, any way?
|
Post Reply
|
Author:
KCRoto (MO)
Any time that someone needs a floor drain they are better served by cutting the floor to do so. When the floor is repaired the floor can be properly pitched to allow for drainage. Using an indirect waste isn't an ideal choice as the floor is never sloped toward the drain; In some cases I have seen a raised edge of tile installed that actually prevent water from flowing inside from the surface.
|
Post Reply
|
Author:
KCRoto (MO)
I think they want to find a way to direct the waste to the triple sink drain instead of a floor drain altogether is what I am getting.
|
Post Reply
|
Author:
440molson (OH)
I believe they didn't want to install a floor drain, if the 3 comp. drain could clasify as a floor drain also.
|
Post Reply
|
Author:
440molson (OH)
Yes. They want to mop the floor to the sink drain, instead of installing a floor drain. If the floor drain is needed they want to know if it can be tied into the interceptor.
|
Post Reply
|
Author:
440molson (OH)
Ok, sorry about the if's, and's, but's. The issue is, does the kitchen floor drain need to tie into the interceptor (grease waste), or can it go out the sanitary waste. I didn't have all of the info. until now.
Thanks again, in advance, Marc
Edited 1 times.
|
Post Reply
|
Author:
KCRoto (MO)
[publicecodes.cyberregs.com]
1003.3.1 Grease interceptors and automatic grease removal devices required.
A grease interceptor or automatic grease removal device shall be required to receive the drainage from fixtures and equipment with grease-laden waste located in food preparation areas, such as in restaurants, hotel kitchens, hospitals, school kitchens, bars, factory cafeterias and clubs. Fixtures and equipment shall include pot sinks, prerinse sinks; soup kettles or similar devices; wok stations; floor drains or sinks into which kettles are drained; automatic hood wash units and dishwashers without prerinse sinks. Grease interceptors and automatic grease removal devices shall receive waste only from fixtures and equipment that allow fats, oils or grease to be discharged.
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
quote; if the 3 comp. drain could clasify as a floor drain also.
I suppose it could, IF you can sink it into the floor so the rim is even with the floor, but then it would be hard to wash dishes in it. HOW could a sink 36" ABOVE the floor be called a floor DRAIN?
|
Post Reply
|
Author:
hj (AZ)
It can go to either one, DEPENDING on what is going to drain into it. The way you are posing the question and subsequent postings is starting to get VERY confusing. HOW is this 3 compartment sink connected to the interceptor?
|
Post Reply
|
Author:
m & m (MD)
The 'sink drain' that he refers to is the floor sink that receives the indirect discharge from the 3 compartment sink above it.
|
Post Reply
|
Author:
hj (AZ)
If that is the case, he kept it VERY secret in the previous posts, especially when he said they did "WANT TO CUT THE FLOOR TO INSTALL A FLOOR SINK". But, if he is referring to a floor sink, then it is obvious that it is also a floor drain, unless it is raised above the floor level, in which case the question makes no sense.
|
Post Reply
|
Author:
440molson (OH)
Thanks everyone for your posts. Again, I am sorry about he confusion. The job was for an additional 2 comp. sink to the existing 3 comp sink(existing above ground interceptor). The first bid was involving an inground interceptor outside. To cut cost, the other choice was to put an above ground inter. at the new 2 comp. sink. The issue was if the floor drain needed to be tied into the grease waste, or not. If so, then the outdoor interceptor would have been the way to go.
Thanks again, Marc.
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
is a completely different situation than we have been working on. And, you did not tell us any of that until now.
|
Post Reply
|
Author:
440molson (OH)
I was not given all the information at first either. It helps when you have all the details.
|
Post Reply
|
Author:
hj (AZ)
quote; It helps when you have all the details
Sort of like giving directions about how to fix a VW, and then they tell you it is a Bentley.
|
Post Reply
|
Author:
packy (MA)
"then they tell you it is a Bentley"
or even worse a ford F450..
|
Post Reply
|
Author:
hj (AZ)
I wouldn't know. The 450 is working in a field in Mexico.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|