Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Example of code versus good practice
Author: bernabeu (SC)

Quote

Thousands of gallons of water cascaded down stairwells and poured through light fixtures of the Stovall on Bayshore Boulevard on Nov. 4 when a worker, about to fall off scaffolding, broke a sprinkler pipe that he had grabbed to steady himself.



Piping was code compliant ~ however ~ 'good practice' dictates:

Piping supports / hangers shall bear the weight of the pipe PLUS 250 lbs.



millions of $$ in damage to be, hopefully, paid by insurance

see: [web.tampabay.com]

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

I think you will find that he probably grabbed a sprinkler branch line to an individual head and those are SELDOM supported by anything other than the piping, unless it had to be repositioned a distance from the main.

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

each head must be supported within 12"

THAT is code

I am referring to the STRENGTH of said hanger and piping

the CPVC pipe which today IS code compliant will not ITSELF meet good practice


in the old days when we did sprinklers (yes, I 'scabbed' as a sprinkler fitter) we used to test the job by doing pull-ups on the piping ~ if it 'wobbled' it failed

................siiiiigh

smiling smiley

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

Many are NOT offset more than 12", but if someone were falling and grabbed a head on a 12" nipple, it WOULD snap off.

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

so ..... a 12" length of 1" steel pipe would not support your weight ?

or enable you to 'catch your balance' so you did not fall ?


GO ON A DIET AND GET UNDER 250

have a good laugh

frowning

ps.

Quote

... he had grabbed to steady himself.



==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 2 times.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

Not if I were falling off a scaffold and it would depend on how much I weighed.

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

posts crossed

we all get my drift re: MINIMUM code versus good/accepted industry practice

the fault may be with the design engineer's SPECIFICATIONS or the contractor saying 'but it meets code'

IMO: the contractor should follow specs providing that they (the specs) are code compliant

not

reduce the specs to the minimum code level

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Example of code versus good practice
Author: packy (MA)

quote..
"hangers shall bear the weight of the pipe PLUS 250 lbs."
so, who in the world weighs every piece of pipe in order to install hangers?
you use some sort of beam hangers, lengths of 3/8 thread rod and 1A band hangers spaced the proper distance apart. (in the real world that is)..

bernabeu, i appreciate your union training but if i ran my business to your standards, i'd be in the bread line..

Post Reply

 Re: Example of code versus good practice
Author: KCRoto (MO)

The entire setup may have been 'good practice' when it was installed, but age and the environment affect metal as well as the waistline of many people.

Post Reply

 Re: Example of code versus good practice
Author: sum (FL)

Is it required for a tub spout (plastic one made by best practicing Price Pfister) to withstand the weight of a grown man after eating a full Thanksgiving meal, using it as a step up to reach the ceiling to remove the exhaust fan cover? big grin

Post Reply

 Re: Example of code versus good practice
Author: KCRoto (MO)

I feel like there is a story in there somewhere..

Post Reply

 Re: Example of code versus good practice
Author: Fixitangel (NC)

Sigh. In the good old days thay made car bumpers of heavy gauge steel; some had chromed dagmars like the ones on HJ's 1950's Mercury:


Now THATS a real bumper smiling smiley Wonder why they don't make them that way anymore? Playing the devil's advocate, I notice there was no mention in the article if the worker on the scaffold was unsteady from drinking or drugs, or if the scaffold was secure and steady with proper safety equipment in place, etc. causing him to loose his balance in the first place.

Final though: if "proper" steel pipe was used in the 1950's (which I assume would be galvanized) isn't there a chance that over many years, the inside of the pipe would develop rust which could either clog the sprinklers or restrict the water flow to them in the case of fire?

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

I have NEVER owned a Mercury. My first car was a NEW 1954 Lincoln convertible. Black with a white top and yellow leather upholstery.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

1l Is the drop ear elbow secured
2. Is it screwed on to a brass nipple
3. Is the hole in the wall a snug fit for the nipple
IF so, then there is little strain on the nipple, but the spout could snap at the thread. What's wrong with your wife doing it? She probably weighs less, and if it breaks she could probably use the "recovery time", while you wait on her.



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

Quote

Final though: if "proper" steel pipe was used in the 1950's (which I assume would be galvanized) isn't there a chance that over many years, the inside of the pipe would develop rust which could either clog the sprinklers or restrict the water flow to them in the case of fire?



Sprinkler pipe is NOT galvanized. It is 'standard' mild black steel (forgot the ASTM #s).

Since the internal water is 'stagnant' (in the sense of no flow except for periodic testing) there is little 'new' oxygen introduced to cause significant rusting.

Proper sizing (maximum of 2 heads on a 1" pipe which is also the minimum pipe size) eliminates the 'clogging' issue.

To my personal knowledge there has NEVER been a failure to perform from a PROPERLY INSTALLED, PROPERLY MAINTAINED, and PROPERLY OPERATED fire protection sprinkler system.

ps. I formerly held a W-12 Certificate of Fitness issued by the NYC Fire Department. (there were only about 100 at any given time)

Said 'cert' entitled me to maintain and operate ANY fire suppression system in NYC.

Installation was done by LICENSED and BONDED contractors.

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

packy,

Quote

...you use some sort of beam hangers, lengths of 3/8 thread rod and 1A band hangers spaced the proper distance apart.



yep

of course

as per specs (which exceed code)

said hangers are designed for and WILL hold over 250 # ANYWHERE on the piping when properly spaced

or

any NON lead expansion shield into the concrete slab/ceiling/deck

any 'carriage screw' into structural framing

we learned the theory to 'get a grasp' of the reasons behind proper procedure, which we then followed on 'autopilot'

of course we did not 'measure' the capacity in the field

we simply installed the hangers where they were necessary

the 'olden days' piping could be used as ladders when climbing around in hung ceilings and 'interstitial' spaces

ps. we called them beam clamps





==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

quote;the inside of the pipe would develop rust which could either clog the sprinklers or restrict the water flow to them in the case of fire?
Reply To This Message

Sprinkler head are NOT connected to the bottom of the main where that could happen. They go up off the top and then drop down to the head. However this does introduce more "failure" points that could fail under stress, although in normal circumstances they do not encounter that level of stress, unless impacted by some moving object. As far as "stagnant water" in a sprinkler system, it IS some of the nastiest water you will ever encounter.



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

good practice re: hangers ~ surpassing code ~ do pull-ups!



code minimum 'glued' CPVC:




I realize the 'good old days' are long gone

however

the 'new stuff' leaves NO MARGIN for error and actually, in many cases, requires MORE experience to install PROPERLY as per actual manufacturer's specs

the above flood would be a case in point

imagine a fire suppression system installed in such a manner that it did not withstand a worker's 'grab for balance' even if it was over 100 lbs force to stop his fall

? what about the stress of expansion and contraction during an actual fire event requiring more than one sprinkler (proper term for a head) to activate ?


enough ..... the horse is long dead

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Example of code versus good practice
Author: BigReg1500 (CT)

I'll bet if you follow the story long enough, someone will try to pin the blame on the worker or his firm for falling off the scaffold.

Was the scaffold set up per the manufacturer's specs and in compliance with OSHA regs?
Did the employer provide fall arresting gear for the worker?

I'm sure the list can go on and on

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

Out here, when you say 'sprinkler' you have to differentiate between a fire sprinkler or a lawn/irrigation sprinkler, because many of our homes have both.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

They will 'pin the blame' on whoever has the best insurance coverage. Like police departments, they don't want the truth as much as they want to clear the case.



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: sum (FL)

In a prison, they will have very strong bars overhead and across doorways able to withstand impact and anyone wanting to do chin-ups. No plastic pipes

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

They also do not have toilets or sinks with faucets they can take apart and flood the area.

Post Reply

 Re: Example of code versus good practice
Author: Fixitangel (NC)

My apologies, sir. My point was; it has a REAL bumper. Was the chrome hood scoop standard?

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

That looks just like the front of my convertible and yes it was standard. I once had a guy cut me off that those "Dagmars" just missed him.

Post Reply

 Re: Example of code versus good practice
Author: sum (FL)

fixitangel would you like some spiked wheels to go with that bumper?





Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: bernabeu (SC)

NO power steering!



==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 1 times.

Post Reply

 Re: Example of code versus good practice
Author: hj (AZ)

My Lincoln had power steering and one of the first power brake systems. When the dealer took us out for a ride in it, he hit the brakes and almost threw all over the windshield.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.