Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 T&P goes straight into the slab
Author: Golden (VA)

Hi everyone. I'm guessing this must be old code but I've come across 2 different water heaters that have the T & P valve drained into the slab or into a wall in a townhouse. It is three-quarter inch copper. the houses were built in the early eighties. if I remember right the T & P valve should terminate so that you can tell if it has opened to alert you to a problem or also for testing. my question is should I cut this line when I replace the heater so that the t & p line is easy to see and just place a catch vessel under it so it can be monitored. also there is an AC Evaporator right next to the water heater and I'm wondering if I can drain it into the old T & P line that runs under the slab or if I can make that old line into an open drain and run them both into it from above? Thanks for any suggestions.

Post Reply

 Re: T&P goes straight into the slab
Author: North Carolina Plumber (NC)

Our code requires that the T + P relief valve must discharge in the same room as the heater. Then it can go into a pan that's piped outside, or into a funnel with an air gap.
In your case I'd cut the pipe, add a funnel to the pipe that runs out and drop the pipe from the new heater into the funnel. I usually make them from a 1 1/2" X 3/4" copper reducing coupling.

Post Reply

 Re: T&P goes straight into the slab
Author: hj (AZ)

we have to discharge it to a location where it will not cause property damage in case of a discharge, which usually means through the wall to the exterior of the building. Your underfloor line probably goes to a point outside the building, and since it should always drain "downhill" the end could be buried undergrounw, I have seen it happen many times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.