Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

I want to add a 3 inch y to my existing 3.5 inch cast system , is there a way to do it that keeps the mainline 3.5 inch ID

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: hj (AZ)

There is not, and never has been, a 3 1/2" cast iron pipe size. It is even rare in steel piping and was usually only used for steam heating systems.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

Its amazing that people think they know everything. It is 4.25 outside dia, it is made of metal, once I find someone that knows what they are talking about, I will cut it open and send you a pic . That way you will be wiser and maybe not so arrogant next time, Apparently there is 3.5 PVC so I will look for that at the wholesaler.Thats unless someone that truly knows about my pipe and could give me a better idea.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: hj (AZ)

In the USA you will look a LONG time before you find a piece of 3 1/2" PVC, and NEVER a piece of steel 3 1/2". How long have you been doing plumbing that you are so wise. I am basing my answer on 60+ years doing it.And once you DO find that 3 1/2" PVC, where are you going to find a "sanitary Y" to fit it?



Edited 1 times.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: Doug E. (CA)

everybody calm down....it's just pipes. lol

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

I am not a plumber and if I can find the 3.5 inch pvc, I am sure they would have the fittings too. now as a 60yr plumber, what would you do to tie into my pipe, size up to 4" abs Y or restrict it down to a 3 inch, either would cause a bulge in or out. I have found the ID by reading another post that said he had cast pipe that was 4.25 OD and the ID was 3.5

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: steve (CA)

Service weight cast iron has an OD of 4.3". Could that be what you have?

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

That must be right, how to best connect into it with abs Y

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: Doug E. (CA)

prefab your wye with two 6" cut pieces glued and set into the wye.
measure that entire length. Add almost a half inch to that measurement
and remove that much of the existing CI pipe. with the appropriate
CI to plastic shielded band make the connection by sliding the metal
portion back onto the CI and rolling the rubber onto your ABS stubs.
grade the wye past level and tighten to 60 in/lbs of torque.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: bernabeu (SC)

Quote

...he had cast pipe that was 4.25 OD and the ID was 3.5




That would be nominal 4" service weight cast iron.

see advice just above

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: packy (MA)

you cut in a cast iron "Y" using no hub couplings and transition to plastic at the branch of the "Y"..

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: hj (AZ)

I would have to see it. You will NEVER find any drain fittings for 3 1/2" pipe, regardless of what you THINK. However, I would use a 4" No-Hub cast iron Y, (which has a 3.94 id and 4.30 o.d.) rather than a plastic one which will have a 4" i.d and 4.50 o.d.



Edited 1 times.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: packy (MA)

hj, guess what???
in MA it is illegal to add a plastic fitting into a cast iron stack. must use 'like' material. so, we are required by code to use a cast iron fitting when adding to a cast iron stack.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: hj (AZ)

Here, you can make ONE transition between materials, but then have to continue with the new one. However, since it is almost easier to install a cast iron tee, in any material, that is what I would choose to do. But if he is going to insist on working with 3 1/2" material, there is no hope for dissuading him. As Bull Halsey said, "Damn the torpedoes, full speed ahead".



Edited 1 times.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

I am just going on internet info to arrive at 3.5 inch ID, now I am wondering if its just thin wall 4 inch cast, that would make more sense being 4.3inch OD, will need to be prepared for anything since I am cutting into the mainline going to the road and the house will be out of order until its done, hopefully I can just add a 4 inch Y and continue from there. What do you people think I should run to my toilet through the slab, 4 inch or reduce it to 3 inch. Is there an advantage to keeping it 4 inch , I am also adding a washer, bath and kitchen sink on the same line. Thank you

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: packy (MA)

run 3 inch below the slab. it will be more than adequate.
when you get to the toilet, use a 4 x 3 elbow with the 4 inch facing up. stick a piece of 4 inch plastic out of the floor a few inches. then pour the slab and tile the floor right up against the pipe sticking out of the floor. for finish, get a flange that fits inside 4 inch pipe. cut the stub flush with the floor and glue the flange inside the pipe so it sits on the floor.
by the way, when you cut out a piece of your underground pipe, cut it carefully so if you run into a problem with sizes you can just re-install the piece you cut with rubber couplings. better to be safe..

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: sum (FL)

yes I would do what packy says to cut it with a cast iron blade and make a nice square cut, I found that putting a hose clamp all the way around really helps to make a nice guide for that. If you make two square cuts you have the mending piece you need in an "emergency" situation. I will say if you CI pipes are very old you may be suprised when you look in the inside it may be corroded and with debris buildup over the years you may not see the round "ID" anymore but more like the inside of a cave.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: KCRoto (MO)

^ don't play with the stalagmites.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: hj (AZ)

and don't stand under stalactites.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

if I find it like a cave, should I flush it with a high pressure hose or will that just cause it to pile up and clog, drain cleaner ??, I am only about 20 feet from the city pipe and 25 feet pipe going into the house from cut

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: bernabeu (SC)

Quote

...you cut in a cast iron "Y" using no hub couplings and transition to plastic at the branch of the "Y"...



DITTO

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: hj (AZ)

The stalagmites and stalactites will be metal and there is almost nothing, other than high powered equipment, which will remove them.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: sharp1 (IL)

If Bull Halsey said that, he was quoting Admiral David Farragut at the battle of Mobile Bay. (I am just now reading a biography of him.)

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: beamvacman (Non-US)

its not really a cave and your stalactites are sludge , how best to clean it out

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: bernabeu (SC)

if it drains ok leave it alone

the 'sludge' may be holding the piping together

wink

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: KCRoto (MO)

The original corrosion forms as the metal oxidizes in the presence of moisture, but after it forms the layer of corrosion, it stops, leaving the underlying metal intact. Removing all that corrosion(provided you could) would simply leave the intact metal prone to oxidation and weakening the pipes.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: sum (FL)

There is a way to rim you CI pipe. It requires special equipment using a high pressure jetter with a chain flail cutting head.

I am not a plumber just a DIYer but two years ago I had this done to my CI lines and I had a few threads discussing it with pics. Here is such a thread.

[www.plbg.com]

It was a job over $2000 which I later on regret doing. There were so many things that went wrong with that job...but that's about right with almost every experience I had with hiring out plumbing work in South Florida.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: vic (CA)

Sum with you not being a plumber I want to thank you as you've shared a lot of your experiences with us and most of us have learned something if not a lot from reading your posts. Thank you.

Post Reply

 Re: Cast sewer 3.5 ID 4.25 OD adding Y
Author: sum (FL)

vic thanks for the kind words I am not sure there is much to learn from me except what NOT to do or don't hire who Sum hired LOL!

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.