Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Pressure regulator valve question
Author: DHD (GA)

Just had the PRV changed at our house. Pressure coming into house before PRV is 160. Back of house around 55 to 60. My concern is that a couple of times a day it will spike to 75 - 80 for no apparent reason. It then settles back down to around 55. Today we were gone for 5 or 6 hours, no one else at home and the pressure was at 75, it peaked while gone to 85. Never came back to 55 until I flushed a toilet. I left the pressure gauge on to monitor.

Is this thing working correctly. It's 4 days old.

Thanks

Post Reply

 Re: Pressure regulator valve question
Author: packy (MA)

water heater firing up, and heated water is expanding?
be happy the pressure does not drop as that would indicate a leak...

Post Reply

 Re: Pressure regulator valve question
Author: hj (AZ)

If it goes up overnight when no one is using the hot water, that would indicate that it is not operating properly.

Post Reply

 Re: Pressure regulator valve question
Author: KCRoto (MO)

unless the last water used at night was hot water such as someone taking a shower.

Post Reply

 Re: Pressure regulator valve question
Author: DHD (GA)

Just checked and there was no air pressure in the expansion tank, no water coming out of the schrader valve either. Pumped it up to 45#. I can see on the pump that air is in when I removed the pump to check again, no air. Went through this several times, same result. The unit is a Watts PET 5. Now what?



Edited 1 times.

Post Reply

 Re: Pressure regulator valve question
Author: KCRoto (MO)

You need a thermal expansion tank added to the system. It is evident you don't have one if you have pressure spikes after installing a prv. The prv closes the system and and when the volume of a system is constant, temperature increases cause a pressure increase. Since you need to alleviate the pressure, you can either eliminate the temperature change, or you can install a thermal expansion tank to increase the volume when the pressure exceeds the pressure in the tank. Or never use hot water again.

Post Reply

 Re: Pressure regulator valve question
Author: DHD (GA)

I have an expansion tank.

I spoke with Watts this morning(after I posted) and they said to remove the tank and then fill with air. Tank is filled with water and something about negative pressure in a closed system. The bladder could have drained gradually over time.



Edited 1 times.

Post Reply

 Re: Pressure regulator valve question
Author: KCRoto (MO)

make sure to charge the tank to 5 psi over gauge pressure when you open a faucet, then close it. That way any excess pressure is relieved.

Post Reply

 Re: Pressure regulator valve question
Author: hj (AZ)

YOU cannot "pressurize" the tank with air, unless you either turn off the water and drain the system or remove the tank from the piping.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.