Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
michdrz (PA)
I'm looking to buy a house that was built in 1965. The heating system has a new gas boiler with the original radiant heating units in each room. The units are about the size of an old cast iron radiator but they are mounted on the wall just above the floor.
Can I easily have these units changed to regular slantFin or Runtal baseboard heaters that run along the base board?
I have a picture but don't know how to post it.
Thanks!
|
Post Reply
|
Author:
Paul48 (CT)
Easy? What's the heat loss of each room? What's the output of the baseboard you want to use? Is there a basement, or is it slab construction? How many floors? How many zones? Many questions would have to be answered in order to answer your question.
|
Post Reply
|
Author:
hj (AZ)
Qnce you know the BTU capacity of the convector, then you install the equivalent amount of baseboard.
|
Post Reply
|
Author:
Paul48 (CT)
You could, but you might be repeating someone elses mistake. The house may suffer from terribly uneven heat already. It would be better to do it from scratch. If, for instance, you'd like to install a HE boiler down the road, you would want to over-radiate each room equally.
|
Post Reply
|
Author:
m & m (MD)
"...If, for instance, you'd like to install a HE boiler down the road, you would want to over-radiate each room equally..."
Please explain.
|
Post Reply
|
Author:
Paul48 (CT)
You'd shoot for about 140* supply temps at a design day temperature. You might only have a few days at that temp during a winter. HE boilers and mod/cons in particular want cool return water temps to keep them in condensing mode, when they are most efficient. The baseboard manufacturers give you the output at different temps, and the lower output requires over-radiating.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|