Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
Lookin4Answers (CA)
I am trying to add a shower drain to an existing line. I am wondering if the following will be within code in California and actually work?
This is the current set-up:
It was a vanity with two sinks. The drain (2 inch) goes straight down and the vent (1-1/2 inch) goes straight up:
[s24.photobucket.com]
This is what I would like to do:
Red = 2" Shower drain, connected with a 2 x 2 x 2 wye.
Green = 2" Wet vent
Yellow = 1-1/2" Vanity drain, connected with a 2 x 1-1/2 x 1-1/2 T.
Blue = 1-1/2" vent to roof
[s24.photobucket.com]
I am getting rid of the other vanity drain on the right side.
Any help is appreciated.
Edited 4 times.
|
Post Reply
|
Author:
packy (MA)
my code does not allow the vent to be reduced to 1 1/2..
must stay full size thru the roof.
|
Post Reply
|
Author:
Lookin4Answers (CA)
Is that because I'm linking 2 things to one vent (vanity and shower)?
|
Post Reply
|
Author:
steve (CA)
California code doesn't state it can't be reduced. It states the dry vent section is sized
per Table 702.1 and 703.2 and those Tables allow for 1½" dry vent.
Scroll down to Section 908.0 and look at 908.1, 908.1.1, 908.1.2, 908.2, 908.2.1 and 908.2.2., for wet vent requirements.
[www.iapmo.org]
|
Post Reply
|
Author:
hj (AZ)
we use a 1 1/2" vent all the time. It has been decades since I have installed a 2" vent on a lavatory or shower, But, if I am reading the picture correctly you CANNOT connect the shower with a "Y".
|
Post Reply
|
Author:
packy (MA)
steve, that is why i qualified my response by saying "my code"...
|
Post Reply
|
Author:
hj (AZ)
But, the person does NOT know if "your code" applies to him, which is why we add qualifiers.
|
Post Reply
|
Author:
North Carolina Plumber (NC)
As long as it's not being used to vent the toilet , 1 1/2" is fine here in NC.
|
Post Reply
|
Author:
m & m (MD)
The existing lav drain is connected to the stack by a combination Y & 1/8th, not a sanitary tee as code ("my code"] requires.
Edited 1 times.
|
Post Reply
|
Author:
steve (CA)
As m & m stated, a double combo tee was used(wrongly by CA code) in the wall and you need to install a sanitary tee when you change the drain for the single sink.
|
Post Reply
|
Author:
Lookin4Answers (CA)
Thank you everyone for your helpful information. After reviewing the responses please clarify if this sounds right. I can maintain the 1-1/2 inch vent, but I will maintain the 2 inch wet vent. I will connect the shower and lavatory drains using a sanitary tee?
Edited 1 times.
|
Post Reply
|
Author:
steve (CA)
If the shower trap arm is attaching to a vertical drain pipe, then yes to the sanitary tee. And yes to the 1½" dry vent and sanitary tee for the sink.
|
Post Reply
|
Author:
Lookin4Answers (CA)
Thank you so much.
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
The connection can be a sanitary tee, Y and 1/8 bend, or combo as long as the lavatory is vented and not using the stack it is connected to as the vent.
|
Post Reply
|
Author:
hj (AZ)
The photo is at the wrong angle and too far away to diferentiate between a double combo or a back to back fixture fitting, but it is immaterial since he is removing the second sink and can easily change it to a sanitary tee when he makes the shower connection.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|