Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Little Giant 6-cia-ml drainosaur cycles on and off
Author: pap (KS)

I am having problems with my diaphragm switch sump pump. Sump pump model is little giant 6-cia-ml / catalog number = 506160 (drainosaur). The sump pump sits in a basin (506065 model wrsc-6). The diaphragm switch went bad so the pump ran constantly. We replaced the diaphragm switch and things appeared to be working again. However, we remembered that the vent pipe wasn't connected. Once we re-connected the vent pipe, we tested the pump again by filling the basin with water. The pump turns on then immediately kicks off and will continue to do this until it manages to pump enough water out. Obviously we can't keep running it this way or it will shorten the life of the pump.

I called little giant and they said the vent pipe must be vented to open air and it sounded to them like the vent pipe to the building wasn't venting to open air somehow. Does anyone have any ideas what we should try to correct the problem? Does it sound correct that the building's vent pipe doesn't vent to open air? If so, I am curious why it was working before the switch went bad in the first place. Is there anything I can do to test or prove that the buildings vent pipe doesn't vent to open air?

thanks in advance

Post Reply

 Re: Little Giant 6-cia-ml drainosaur cycles on and off
Author: hj (AZ)

I could see a pressure switch functioning on and off it it were the air inside an unvented sealed pit because drawing water out would change the pressure. But your switch should be operated by water pressure which does NOT change when the air pressure changes. Therefore, it will take more investigating and testing to determine what is actually happening. Your power cord may have a small "vent tube" from the pressure switch, and if so and it gets moisture in it that will severely affect the operation of the switch.



Edited 1 times.

Post Reply

 Re: Little Giant 6-cia-ml drainosaur cycles on and off
Author: steve (CA)

I think the pressure in the tank being reduced, because of a lack of venting, would cause the pressure switch to cycle. If you look at the reverse of this and pressurized the tank, the water would exert more pressure against the switch, so a vacuum has to have an opposite effect.

Post Reply

 Re: Little Giant 6-cia-ml drainosaur cycles on and off
Author: hj (AZ)

IT would have to "lift" the water which cannot happen. Pressure pushes down on the water which is an entirely different dynamic.

Post Reply

 Thanks for all
Author: pap (KS)

fyi everyone. The pressure differential was indeed the problem. I pipe clamped my wet/dry vac onto the building's vent pipe and let it blow for several minutes. When I connected the pump vent pipe with the building's vent pipe, everything appears to be functioning normally now. Thanks for the replies.



Edited 2 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.