Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 # of dfu's for 2" branch in basement.
Author: golliath (CO)

There is a 2" vertical drain in basement that goes into slab. Customer wants to put kitchen sink(currently fixture for this line), new island sink. In basement they want laundry and laundry sink both tied into this. also there is floor drain upstairs(for dog washing) coming to this 2" line. If i am reading ipc correctly a 2" branch can take21 dfu's with a 1/4" slope. What is your guys take on this? thx,



Edited 1 times.

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: m & m (MD)

What will you do about individual venting of added fixtures?

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: North Carolina Plumber (NC)

Here in NC we can't use a 2" horizontal drain for a washing machine, it must be 3".

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: golliath (CO)

AAV's. also here in Co. washing machine waste is to increase to 3" when it has other fixture tieing into it but havent been called on that yet.

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: golliath (CO)

there is also a vtr at kitchen sink currently which may sufice for island sink that is about 8' away from it. a studor at washer box should be good for both laundry and laundry sink which have dryer between them so only a few feet apart.

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: mr leak (CA)

2 inch should be fine for washing machine drain and AAV valves do fail as they are mechanical and increasingly not allowed

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: hj (AZ)

I am not sure about the IPC, (it pretty much lets you do anything you want to), but our UPC has a maximum of SIX fus on a 2" branch.

Post Reply

 Re: # of dfu's for 2" branch in basement.
Author: Ksherlock (VA)

The IPC is clear to me. A Max. of 6 dfu's in a "branch". 21 dfu is max on the
"building drain." Everything is fine all the way down to where the pipe disappears below the floor. At that point a 2" pipe in inadequate.

Post Reply

 thanks all for input.
Author: golliath (CO)

thanks all for input.



Edited 1 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.