Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
Meridian West (GA)
Here's my situation:
The pressure relief valve on the water heater is weeping (6 years old). I put a Y adapter on the garden hose bib so I can have a pressure gauge with a lazy hand one one leg and let water out of the the other.
Lazy hand said 150 PSI. If I run water, pressure returns to 80, then climbs.
Today with just me here, I checked the thermal expansion tank. It's shot. Air side was full of water and bench testing shows it won't hold pressure.
Turned the water heater off at the breaker to eliminate thermal expansion. No change it behavior at the gauge.
I got the regulator set lower, now at 40 psi. Gauge hovers there for a second and starts climbing. Goes over 100 within 5 minutes.
I think my regulator is shot. What do you guys think?
|
Post Reply
|
Author:
North Carolina Plumber (NC)
I think you are correct in your diagnosis.
|
Post Reply
|
Author:
hj (AZ)
quote; I think my regulator is shot. What do you guys think?
Obviously,and, what else could it be?
|
Post Reply
|
Author:
Meridian West (GA)
A new regulator and expansion tank and we're holding steady at 45 PSI. Mrs. West is unhappy with the reduction in pressure, she had become spoiled with street pressure. (Or is that spoiled further?) Anyway, I may have to crank it up a few pounds. Thanks for the help!
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
When I install them, I DO crank them up to 75-80 psi.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|