Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
elegantny (NY)
I have a hot water system McLain CGA5 gold natural gas boiler with 5 zones controlled with a TACO circulator for each zone. One zone continually has a hot radiator even after I disconnected the thermostat. I was told to look for zone valves but I don't see any. Is the taco being used as a zone valve ? How should I troubleshoot this problem? Any help would be appreciated.
Thank you
Joe
|
Post Reply
|
Author:
packy (MA)
some of the newer taco circulators have an internal flow checks.
see if the model number of the circulator is a 007IFC.
if so the problem is it is sticking. it is easily replaced but you must remove the circulator to do it.
|
Post Reply
|
Author:
hj (AZ)
I assume the pumps are on the return lines. If so, without "flow checks" on the feed lines there is nothing to prevent the water from circulating into the system, at least to the first radiation.
|
Post Reply
|
Author:
greekguy7 (IL)
do u have 5 taco circulators and 5 thermostats? i have seen zone valves in bedroom closets, but that was in multifamily buildings.
do you see any flow-control valves on the supply side? one might be stuck open... tap it with a rubber mallet
Edited 1 times.
|
Post Reply
|
Author:
elegantny (NY)
Do I have to change the whole circulator or just the flow checks?
|
Post Reply
|
Author:
greekguy7 (IL)
first check if u have a taco 007... or a taco 007-ifc. check the label on it
|
Post Reply
|
Author:
elegantny (NY)
To Greekguy
Yes 5 circulatory & 5 thermostats in a single family house.
|
Post Reply
|
Author:
packy (MA)
just the flow check.
look carefully at this picture. see the white plastice object in the top of the circulator. that is the flow check. you grab it with a big needle nose pliers, twist it and it pulls right out. you may simply find debris in the flow check, clean it and put it back and be all set.
|
Post Reply
|
Author:
elegantny (NY)
Packy
Thank you I will try that and keep you updated
|
Post Reply
|
Author:
bernabeu (SC)
suffix "ifc" means internal flow check
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
elegantny (NY)
Packs
Finally had a chance to check it it is a Taco 007FS.Removed the unit no white plastic flow checks, removed the housing no internal parts serviceable it seems like a sealed unit.
Thanks
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: