Author:
dirtymartini (VT)
Serious,
The maxinum loop length for 5/8 inch pex (SDR-9) is 450 ft.
Here is a link that explains PEX nicely.
[www.@]
|
|
|
Author:
dlh (TX)
The URL is not valid and cannot be loaded. is the message i got
i wouldnt run 5/8 pex that far because that most likely is the outside diameter and that means the inside is less than 1/2" and that is a mighty long distance to run that small of pipe and have move than a lavatory sink running off it. now if it is 3/4" O.D. then yeah it might work but id rather go a hair to big than regret it later. its not that much more in materials pricing and the labor should be about the same
----------------------------
PLUMBERS "Protecting The Health Of The Nation"
|
|
|
Author:
Shoemaker2 (MA)
I am guessing he is talking heat loops.
|
|
|
Author:
dlh (TX)
well in that case then you might be right as i dont know heat
----------------------------
PLUMBERS "Protecting The Health Of The Nation"
|
|
|
Author:
nhmaster3015 (NH)
450 is max, I like to keep them to 300-350 for radiant loops.
|
|
|
Author:
Scott D. Plumber (VA)
agree, stick with 300'. You can use a lower energy pump that way.
***********************************